Difference between revisions of "Zone Motion Controllers"
(Content 2.0 change and registered trademark addition)
(Re-written for clarity and images added)
Zone Motion Controllers is designed to combine multiple motion sensors to act as one “zone” for triggering actions in Rule Machine<sup>®</sup> and other apps. Creating zones is helpful because it can create motion coverage that a single motion sensor cannot do. Zones can also be used to help eliminate false motion from triggering your lights and automations. This is done creating motion zones made up of two or more motion sensors.
Zone Motion Controllers is designed to combine multiple motion sensors to act as one “zone” for triggering actions in Rule Machine<sup>®</sup> and other apps. Creating zones will allow multiple motion sensors to work together to achieve a desired effect within the zone. Zones can be used to help eliminate false motion from triggering your lights and automations, they can prevent lights from turning off in large or obstructed spaces where a single motion sensor might not continuously detect your presence, or they can prevent motion sensors from activating until triggered by another source, such as a door sensor.
Once a Motion Zone is created, it can be used selected as a motion sensor in Rule Machine<sup>®</sup> and other rule building apps to trigger actions.
Once a Motion Zone is created, it can be selected as a ''mZone'' motion sensor in Rule Machine<sup>®</sup> and other apps to trigger actions.
There are three types of motion zones you can create with Zone Motion Controllers.
Here's how to get started with Zone Motion Controllers:
=='''Create a Triggered Activation Zone'''==
This type of zone allows multiple sensors to act together as unit. It requires two corresponding events to activate. First the zone needs to be enabled by a trigger, which can be a motion sensor, contact sensor, switch or vibration sensor. Once the trigger enables the zone, the zone will be activated if one of the motion sensors is triggered within the selected activation window. The zone will stay activated as long as any of the motion sensor detect motion within the selected Activity Timeout window. Each detected motion resets the activity timeout. (In other words, the zone stays active until X minutes after the last motion was detected)
Here’s how to set it up:
=== Installing the Zone Motion Controllers app ===
#Open the Zone Motion Controllers app in the Hubitat Web interface.
# From the Hubitat Web Interface select '''Apps'''[[File:Install Built-In App 2.0.png|none|thumb|600x600px]]
#Click ''Create New Motion Zone''.
# Choose Zone Motion Controllers from the list of Hubitat Elevation™ Built-In Apps[[File:Install Zone Motion Controllers.png|none|thumb|600x600px]]
#Give your zone a name.
#Select the motion sensors you would like to include in the motion zone for the ''Motion Sensors'' box and click ''update''.
=== Creating a New Motion Zone ===
#Select ''Triggered Activation'' in the ''Zone Type'' dropdown menu.
#Select the Activation Window from the dropdown menu.
#Click ''Trigger Devices'' to select the motion sensors, contact sensors, switches or vibration sensors you want to trigger the activation window. When you select a device, you may be offered additional options for activation, such as whether to activate when a door opens or closes.
#Select the ''Activity Timeout'' window from the dropdown menu. The zone will stay activated until motion has not been detected for the number of minutes you select.
#If you only want the motion zone to work in certain modes, select them under ''Set for specific mode(s)''.
#When your motion zone is finished, click ''Done''.
=='''Create a False Motion Reduction Zone'''==
==== '''Create a False Motion Reduction Zone''' ====
A False motion reduction zone can help prevent motion lights being triggers accidentally by pets or sunlight because it requires two or more motion sensors to activate before the motion zone is triggered. Set your motion sensor far enough apart that your pet can't cross both paths at the same time, but a human will.
A ''False Motion Reduction Zone'' can help prevent lights from being triggered accidentally by outdoor interference from clouds, sun or aliens. Motion detectors are typically placed with two or more pointing at your target area. When the specified number of sensors all detect motion, then the zone becomes active and triggers your lights, device or automation. You might also use this in an indoor situation where a pet cannot be detected by both sensors at the same time, but a human would.
#Open the Zone Motion Controllers app.
#Click ''Create New Motion Zone.''
#Select '''Create New Motion Zone'''[[File:Zone Motion Controllers - Create New Motion Zone.png|none|thumb|600x600px]]
#Name your Motion Controller Zone. '''''NOTE''': You may wish to add a description to the name for the type of motion zone you are creating, so when you are selecting them in Rule Machine<sup>®</sup> for example, the type of zone you create will not be confused with another type for the same zone.''
#Select the motion sensors you would like to include in the motion zone.
#Select '''False Motion Reduction''' in the ''Zone Type'' drop-down menu[[File:Zone Motion Controller naming.png|none|thumb|600x600px]]
#Select ''False Motion Reduction'' in the ''Zone Type'' dropdown menu.
#Select the motion sensors you would like to include in the motion zone and then set the '''Activation Window''' from the dropdown menu. This is the amount of time all motion sensors specified in the zone must detect movement before the zone will activate.[[File:Zone Motion Controllers FMR Sensors and activation window.png|none|thumb|600x600px]]
#Select the ''Activation Window'' from the dropdown menu. The zone will activate ONLY if the minimum number of motion sensors are active within the number of seconds you select for the activation timeframe.
#In the '''Minimum Active Threshold''' field, enter the number of devices required to activate the zone. The must be 2 or more motion sensors you selected in the previous step. The result will be that the motion zone will become active, ONLY if the minimum number of motion sensors detect movement within the number of seconds you chose for the activation timeframe.[[File:Zone Motion Controllers FMR minimum active threshold.png|none|thumb|600x600px]]
#In the ''Minimum Active Threshold'' field, enter the number of devices required to activate the zone. The should be a number between 2 and however many motion sensors you selected in step 4.
#If you only want the motion zone to activate in only certain modes, choose them under '''Set for specific mode(s)'''. If you don't make a selection, then the motion zone will be active in all modes.[[File:Zone Motion Controllers active mode selection.png|none|thumb|600x600px]]
#When your motion zone is finished, press the '''Done''' button.
=='''Create a Motion Aggregation Zone'''==
===='''Create a Motion Aggregation Zone'''====
A motion aggregation zone activates whenever any one of the motion sensors in zone are activated. The zone will stay active as long as any one of the motion sensors are active within the selected Activity Timeout. Each motion activity will reset the Activity Timeout. (In other words, the zone stays active until X minutes after the last motion was detected by any of the sensors).
A ''Motion Aggregation Zone'' activates whenever any one of the motion sensors in a zone are activated, and it will remain active until all the motion sensors in the zone are no longer detecting movement and the '''Activity Timeout''' period has not expired. Each time motion activity is detected by any motion sensor within the ''Motion Aggregation Zone'', it will reset the ''Activity Timeout'' period. This type of zone is ideal for large or odd-shaped rooms where multiple motion sensors are required to provide ample coverage, allowing them to work together as team to keep you from being unexpectedly left in the dark.
This type of zone is ideal for large or odd-shaped rooms where multiple motion sensors are required to provide ample coverage.
#Select '''Motion Aggregation''' in the ''Zone Type'' drop-down menu.[[File:Zone Motion Controller Motion Aggregation.png|none|thumb|600x600px]]
#Select the motion sensors you would like to include in the motion zone and then set the '''Activity Timeout''' period from the drop-down menu. The zone will stay activated as long as there is motion on ANY of the motion sensors within that timeframe. The ''Activity Timeout'' is reset when any motion is detected.[[File:Zone Motion Controllers MA Sensors and Timeout.png|none|thumb|600x600px]]
===='''Create a Triggered Activation Zone'''====
This type of zone allows multiple sensor types to work together in the activation of a motion zone. It requires at least two corresponding events for the zone to activate a device or an automaton. Valid trigger devices may be a motion sensor, contact sensor, switch or vibration sensor. The zone will stay activated as long as there is motion on ANY of the motion sensors within that timeframe. The ''Activity Timeout'' is reset when any motion is detected.
#Select '''Trigger Activation Zone''' in the ''Zone Type'' drop-down menu.[[File:Zone Motion Controllers Trigger Activation.png|none|thumb|600x600px]]
#Select ''Motion Aggregation'' in the ''Zone Type'' dropdown menu.
#Select the ''Activity Timeout'' window from the dropdown menu. The zone will stay activated as long as there is motion on ANY of the motion sensors within that timeframe. The Activity Timeout is reset with every motion.
#Select an '''Activation Window''' from the drop-down menu. This is the time period after a trigger device is activated, that motion detected by the specified motion sensors will still activate the motion zone. If the trigger device activates, but the specified ''Activation Window'' has expired, then the motion zone will not be active, even though the motion sensors may be detecting movement.[[File:Zone Motion Controllers TA Sensor and Activation Window.png|none|thumb|600x600px]]
#If you only want the motion zone to work in certain modes, select them under Set for specific mode(s)
#Press the '''Trigger Devices''' button to select the ''motion sensors, contact sensors, switches or vibration sensors'' you want to trigger the activation window for the selected motion sensors. When you select a device, you may be offered additional options for activation, such as whether to activate when a door ''opens'' or ''closes''.[[File:Zone Motion Controllers Trigger Devices.png|none|thumb|600x600px]]
#Select the trigger devices you would like to enable the motion sensors in the zone and then set the '''Activity Timeout''' period from the drop-down menu. The zone will stay activated as long as there is motion on ANY of the motion sensors within that timeframe, as long as motion was detected before the '''Activation Window''' expired. The ''Activity Timeout'' period will be reset if a trigger devices again activates and the motion sensors detect movement within the ''Activation Window,'' following a trigger event.[[File:Zone Motion Controller TA Activity Timeout period.png|none|thumb|600x600px]]
Revision as of 06:27, 19 December 2018
Zone Motion Controllers is designed to combine multiple motion sensors to act as one “zone” for triggering actions in Rule Machine® and other apps. Creating zones will allow multiple motion sensors to work together to achieve a desired effect within the zone. Zones can be used to help eliminate false motion from triggering your lights and automations, they can prevent lights from turning off in large or obstructed spaces where a single motion sensor might not continuously detect your presence, or they can prevent motion sensors from activating until triggered by another source, such as a door sensor.
Once a Motion Zone is created, it can be selected as a mZone motion sensor in Rule Machine® and other apps to trigger actions.
  2. Choose Zone Motion Controllers from the list of Hubitat Elevation™ Built-In Apps
A False Motion Reduction Zone can help prevent lights from being triggered accidentally by outdoor interference from clouds, sun or aliens. Motion detectors are typically placed with two or more pointing at your target area. When the specified number of sensors all detect motion, then the zone becomes active and triggers your lights, device or automation. You might also use this in an indoor situation where a pet cannot be detected by both sensors at the same time, but a human would.
  1. Open the Zone Motion Controllers app.
  2. Select Create New Motion Zone
  3. Name your Motion Controller Zone. NOTE: You may wish to add a description to the name for the type of motion zone you are creating, so when you are selecting them in Rule Machine® for example, the type of zone you create will not be confused with another type for the same zone.
  4. Select False Motion Reduction in the Zone Type drop-down menu
  5. Select the motion sensors you would like to include in the motion zone and then set the Activation Window from the dropdown menu. This is the amount of time all motion sensors specified in the zone must detect movement before the zone will activate.
  6. In the Minimum Active Threshold field, enter the number of devices required to activate the zone. The must be 2 or more motion sensors you selected in the previous step. The result will be that the motion zone will become active, ONLY if the minimum number of motion sensors detect movement within the number of seconds you chose for the activation timeframe.
  7. If you only want the motion zone to activate in only certain modes, choose them under Set for specific mode(s). If you don't make a selection, then the motion zone will be active in all modes.
  8. When your motion zone is finished, press the Done button.
A Motion Aggregation Zone activates whenever any one of the motion sensors in a zone are activated, and it will remain active until all the motion sensors in the zone are no longer detecting movement and the Activity Timeout period has not expired. Each time motion activity is detected by any motion sensor within the Motion Aggregation Zone, it will reset the Activity Timeout period. This type of zone is ideal for large or odd-shaped rooms where multiple motion sensors are required to provide ample coverage, allowing them to work together as team to keep you from being unexpectedly left in the dark.
  4. Select Motion Aggregation in the Zone Type drop-down menu.
  5. Select the motion sensors you would like to include in the motion zone and then set the Activity Timeout period from the drop-down menu. The zone will stay activated as long as there is motion on ANY of the motion sensors within that timeframe. The Activity Timeout is reset when any motion is detected.
  6. If you only want the motion zone to activate in only certain modes, choose them under Set for specific mode(s). If you don't make a selection, then the motion zone will be active in all modes.
  7. When your motion zone is finished, press the Done button.
This type of zone allows multiple sensor types to work together in the activation of a motion zone. It requires at least two corresponding events for the zone to activate a device or an automaton. Valid trigger devices may be a motion sensor, contact sensor, switch or vibration sensor. The zone will stay activated as long as there is motion on ANY of the motion sensors within that timeframe. The Activity Timeout is reset when any motion is detected.
  4. Select Trigger Activation Zone in the Zone Type drop-down menu.
  5. Select the motion sensors you would like to include in the motion zone for the Motion Sensors box and click update.
  6. Select an Activation Window from the drop-down menu. This is the time period after a trigger device is activated, that motion detected by the specified motion sensors will still activate the motion zone. If the trigger device activates, but the specified Activation Window has expired, then the motion zone will not be active, even though the motion sensors may be detecting movement.
  7. Press the Trigger Devices button to select the motion sensors, contact sensors, switches or vibration sensors you want to trigger the activation window for the selected motion sensors. When you select a device, you may be offered additional options for activation, such as whether to activate when a door opens or closes.
  8. Select the trigger devices you would like to enable the motion sensors in the zone and then set the Activity Timeout period from the drop-down menu. The zone will stay activated as long as there is motion on ANY of the motion sensors within that timeframe, as long as motion was detected before the Activation Window expired. The Activity Timeout period will be reset if a trigger devices again activates and the motion sensors detect movement within the Activation Window, following a trigger event.
  9. If you only want the motion zone to activate in only certain modes, choose them under Set for specific mode(s). If you don't make a selection, then the motion zone will be active in all modes.
  10. When your motion zone is finished, press the Done button.