Difference between revisions of "Zone Motion Controllers"
m (wording edits) (Tag: Visual edit) |
| Line 32: | Line 32: | ||
#Name your Motion Controller Zone. '''''NOTE''': You may wish to add a description to the name for the type of motion zone you are creating, so when you are selecting them in Rule Machine<sup>®</sup> for example, the type of zone you create will not be confused with another type for the same area'' | #Name your Motion Controller Zone. '''''NOTE''': You may wish to add a description to the name for the type of motion zone you are creating, so when you are selecting them in Rule Machine<sup>®</sup> for example, the type of zone you create will not be confused with another type for the same area'' | ||
#Select '''Motion Aggregation''' in the ''Zone Type'' drop-down menu.[[File:Zone Motion Controller Motion Aggregation.png|none|thumb|600x600px]] | #Select '''Motion Aggregation''' in the ''Zone Type'' drop-down menu.[[File:Zone Motion Controller Motion Aggregation.png|none|thumb|600x600px]] | ||
| − | #Select the motion sensors you would like to include in the motion zone and then set the '''Activity Timeout''' period from the drop-down menu. The zone will stay activated as long as there is motion on ANY of the motion sensors within that timeframe. The ''Activity Timeout'' | + | #Select the motion sensors you would like to include in the motion zone and then set the '''Activity Timeout''' period from the drop-down menu. The zone will stay activated as long as there is motion on ANY of the motion sensors within that timeframe. The ''Activity Timeout'' will be reset when any motion is detected.[[File:Zone Motion Controllers MA Sensors and Timeout.png|none|thumb|600x600px]] |
#If you only want the motion zone to activate in only certain modes, choose them under '''Set for specific mode(s)'''. If you don't make a selection, then the motion zone will be active in all modes.[[File:Zone Motion Controllers active mode selection.png|none|thumb|600x600px]] | #If you only want the motion zone to activate in only certain modes, choose them under '''Set for specific mode(s)'''. If you don't make a selection, then the motion zone will be active in all modes.[[File:Zone Motion Controllers active mode selection.png|none|thumb|600x600px]] | ||
#When your motion zone is finished, press the '''Done''' button. | #When your motion zone is finished, press the '''Done''' button. | ||
===='''Create a Triggered Activation Zone'''==== | ===='''Create a Triggered Activation Zone'''==== | ||
| − | This type of zone allows multiple sensor types to work together in the activation of a motion zone. It requires at least two corresponding events for the zone to activate a device or an automaton. Valid trigger devices may be a motion sensor, contact sensor, switch or vibration sensor. The zone will stay activated as long as there is motion on ANY of the motion sensors within that timeframe. The ''Activity Timeout'' | + | This type of zone allows multiple sensor types to work together in the activation of a motion zone. It requires at least two corresponding events for the zone to activate a device or an automaton. Valid trigger devices may be a motion sensor, contact sensor, switch or vibration sensor. The zone will stay activated as long as there is motion on ANY of the motion sensors within that timeframe. The ''Activity Timeout'' will be reset when any motion is detected. |
#Open the Zone Motion Controllers app. | #Open the Zone Motion Controllers app. | ||
| Line 43: | Line 43: | ||
#Select '''Trigger Activation Zone''' in the ''Zone Type'' drop-down menu.[[File:Zone Motion Controllers Trigger Activation.png|none|thumb|600x600px]] | #Select '''Trigger Activation Zone''' in the ''Zone Type'' drop-down menu.[[File:Zone Motion Controllers Trigger Activation.png|none|thumb|600x600px]] | ||
| − | #Select the motion sensors you would like to include in the motion zone | + | #Select the motion sensors you would like to include in the motion zone and press '''Update'''. |
#Select an '''Activation Window''' from the drop-down menu. This is the time period after a trigger device is activated, that motion detected by the specified motion sensors will still activate the motion zone. If the trigger device activates, but the specified ''Activation Window'' has expired, then the motion zone will not be active, even though the motion sensors may be detecting movement.[[File:Zone Motion Controllers TA Sensor and Activation Window.png|none|thumb|600x600px]] | #Select an '''Activation Window''' from the drop-down menu. This is the time period after a trigger device is activated, that motion detected by the specified motion sensors will still activate the motion zone. If the trigger device activates, but the specified ''Activation Window'' has expired, then the motion zone will not be active, even though the motion sensors may be detecting movement.[[File:Zone Motion Controllers TA Sensor and Activation Window.png|none|thumb|600x600px]] | ||
#Press the '''Trigger Devices''' button to select the ''motion sensors, contact sensors, switches or vibration sensors'' you want to trigger the activation window for the selected motion sensors. When you select a device, you may be offered additional options for activation, such as whether to activate when a door ''opens'' or ''closes''.[[File:Zone Motion Controllers Trigger Devices.png|none|thumb|600x600px]] | #Press the '''Trigger Devices''' button to select the ''motion sensors, contact sensors, switches or vibration sensors'' you want to trigger the activation window for the selected motion sensors. When you select a device, you may be offered additional options for activation, such as whether to activate when a door ''opens'' or ''closes''.[[File:Zone Motion Controllers Trigger Devices.png|none|thumb|600x600px]] | ||
| − | #Select the trigger devices you would like to | + | #Select the trigger devices you would like to be responsible for enabling the motion sensors in the zone, and then set the '''Activity Timeout''' period from the drop-down menu. The zone will stay activated as long as there is still motion on ANY of the motion sensors and the ''Activity Timeout'' period has not expired. The ''Activity Timeout'' period will be reset if a trigger devices again activates and the motion sensors detect movement within the ''Activation Window,'' following a trigger event.[[File:Zone Motion Controller TA Activity Timeout period.png|none|thumb|600x600px]] |
Revision as of 06:49, 19 December 2018
Zone Motion Controllers is designed to combine multiple motion sensors to act as one “zone” for triggering actions in Rule Machine® and other apps. Creating zones will allow multiple motion sensors to work together to achieve a desired effect within the zone. Zones can be used to help eliminate false motion from triggering your lights and automations, they can prevent lights from turning off in large or obstructed spaces where a single motion sensor might not continuously detect your presence, or they can prevent motion sensors from activating until triggered by another source, such as a door sensor.
Once a Motion Zone is created, it can be selected as an mZone motion sensor in Rule Machine® and other apps to trigger actions.
Here's how to get started with Zone Motion Controllers:
Installing the Zone Motion Controllers app
- Choose Zone Motion Controllers from the list of Hubitat Elevation™ Built-In Apps
Creating a New Motion Zone
Create a False Motion Reduction Zone
A False Motion Reduction Zone can help prevent lights from being triggered accidentally by outdoor interference from clouds, sun or aliens. Motion detectors are typically placed with two or more pointing at your target area. When the specified number of sensors all detect motion, then the zone becomes active and triggers your lights, device or automation. You might also use this in an indoor situation where a pet cannot be detected by both sensors at the same time, but a human would.
- Open the Zone Motion Controllers app.
- Select Create New Motion Zone
- Name your Motion Controller Zone. NOTE: You may wish to add a description to the name for the type of motion zone you are creating, so when you are selecting them in Rule Machine® for example, the type of zone you create will not be confused with another type for the same area.
- Select False Motion Reduction in the Zone Type drop-down menu
- Select the motion sensors you would like to include in the motion zone and then set the Activation Window from the dropdown menu. This is the amount of time all motion sensors specified in the zone must detect movement before the zone will activate.
- In the Minimum Active Threshold field, enter the number of devices required to activate the zone. The must be 2 or more motion sensors you selected in the previous step. The result will be that the motion zone will become active, ONLY if the minimum number of motion sensors detect movement within the number of seconds you chose for the activation timeframe.
- If you only want the motion zone to activate in only certain modes, choose them under Set for specific mode(s). If you don't make a selection, then the motion zone will be active in all modes.
- When your motion zone is finished, press the Done button.
Create a Motion Aggregation Zone
A Motion Aggregation Zone activates whenever any one of the motion sensors in a zone are activated, and it will remain active until all the motion sensors in the zone are no longer detecting movement and the Activity Timeout period has not expired. Each time motion activity is detected by any motion sensor within the Motion Aggregation Zone, it will reset the Activity Timeout period. This type of zone is ideal for large or odd-shaped rooms where multiple motion sensors are required to provide ample coverage, allowing them to work together as team to keep you from being unexpectedly left in the dark.
- Select Motion Aggregation in the Zone Type drop-down menu.
- Select the motion sensors you would like to include in the motion zone and then set the Activity Timeout period from the drop-down menu. The zone will stay activated as long as there is motion on ANY of the motion sensors within that timeframe. The Activity Timeout will be reset when any motion is detected.
This type of zone allows multiple sensor types to work together in the activation of a motion zone. It requires at least two corresponding events for the zone to activate a device or an automaton. Valid trigger devices may be a motion sensor, contact sensor, switch or vibration sensor. The zone will stay activated as long as there is motion on ANY of the motion sensors within that timeframe. The Activity Timeout will be reset when any motion is detected.
- Select Trigger Activation Zone in the Zone Type drop-down menu.
- Select the motion sensors you would like to include in the motion zone and press Update.
- Select an Activation Window from the drop-down menu. This is the time period after a trigger device is activated, that motion detected by the specified motion sensors will still activate the motion zone. If the trigger device activates, but the specified Activation Window has expired, then the motion zone will not be active, even though the motion sensors may be detecting movement.
- Press the Trigger Devices button to select the motion sensors, contact sensors, switches or vibration sensors you want to trigger the activation window for the selected motion sensors. When you select a device, you may be offered additional options for activation, such as whether to activate when a door opens or closes.
- Select the trigger devices you would like to be responsible for enabling the motion sensors in the zone, and then set the Activity Timeout period from the drop-down menu. The zone will stay activated as long as there is still motion on ANY of the motion sensors and the Activity Timeout period has not expired. The Activity Timeout period will be reset if a trigger devices again activates and the motion sensors detect movement within the Activation Window, following a trigger event.